I have a 322 monterey cruiser. I have a marine air vector A/C.

The issue I am having is the unit will come on and begin to cool down. After cooling for a couple of minutes the unit switche back to fan and stops cooling. This is the cycle it goes thorugh. It never cools long enough to cool cabin down. Also the unit has a digital control panel.

I have checked the following:
1 Freon level
2. Seacock strainers
3. Water discharge
4. Return air filter
all of which are fine

Does anyone have any ideas of what my problem can be?
Thanks for any help you may offer.

Rob
 
Does your control panel have error codes?
You may be getting a high or low pressure shut down.
Or you may have a bad control panel board.
Even if you have a clean strainer with plenty of water coming out, you may have a scaled up heat exchanger,
which will give you a high pressure shut down.
Low freon pressure will shut it down also.
 
did you look at the water discharge out of the hull and make sure it is strong enough? although if it was a flow issue, you'd have a high press. error on the display.
 
Check to see if when the fan is on with no cool air, that the coils have not freezed over.
 
good point on the evaporator freezing but not in a couple of minutes....
 
As I'm reading this my A/C is running off of dockside water. Last evening, the jelly fish clogged my internal filter basket as well as eel grass strainer. The dockside water allowed me to have a comfortable sleep. You may want to see if hooking water supply up like this will keep unit running. If so, you will at least know it's a water supply issue.
 
Low freon pressure will do what you are saying. You will have around 150 psi when not running. It will start up and the pressure will come down until it hits the low pressure shut down.
Or it may be the high pressure shut down due to low water flow or you may have an obstruction in the line. It may be a plugged up high side dryer or a plugged up capillary tube.
If you have a 12K btu unit, you will probably have 3 tubes. If one plugs, your high side will go up cause you cannot get enough freon thru the tubes. You basically are pumping 12K btu thru 8K btu tubes. To check this out, you need to take the cover off of the evaporator and you will see the small tubes. If they are all sweating, then they are all good. If 2 of them are sweating or frosted and one is not, you have one that is plugged.
 
"As I'm reading this my A/C is running off of dockside water."

That seems like an incredible waste of fresh water.

Couldn't you just clean the strainer? Are you having to pay for the fresh water?
 
My 16k unit is off the boat-- again. I saw that the coils were frosting over. I would shut it down, let it thaw, turn it on, and then watch in amazement as the coils would start frosting almost immediately. Starts with one, two, three, four, etc. Usually the result of too low freon or too low air or water flow. In my case, it was a freon leak. He's bench testing it under pressure so that we NEVER have to wrestle that darned thing out again. :-(

Paul
 
As a side note, I place small chlorine tablets in the strainer every so often, helps keep the whole system cleaner. They are available at Wally World for small kiddy pools and such.

Fred
.
 
sounds like you have a number of items to check before calling in the pros from dover. first pull out the installation manual and find out how many gallons per minute of water the system requires. then get a pale and time how much water comes out in 15 seconds, multiply by four and check it against the spec. if you have sufficient water flow, next check the freon level with your hands. the line coming out of the compressor should be so hot you can't touch it, the line going back to the compressor should be cold, but not frozen solid with ice. you should feel the liquid going thru it, but if there are bubbles in the flow after about a minute of run time you are prob low on freon. if all the above checks out, stick your hand in the water stream going overboard, you should feel pretty warm water, if not you probably need to descale the condenser. easily done with a product called barnicle buster. its safe for this application, just follow the directions. if none of the above help, you'll need the pros to check the relays on the control board and put a gauge on the freon level to see exactly what is going on. hope this helps.
 
If you have a clean evap. coil, you can feel the rows of coils or the loops, with your hand, on the ends of the coil. If it is full, you will have cold loops or coils all the way up to the top.
If it is low, you will have some that are not cold at the top.
It is not perfect, but it is close.
If none are cold, it is way too low.
 
When the a/c shuts down whats the set point temp vs the displayed space temp.

could be a bad return sensor.

Rob
 
Capt. Bill1, It is well water that my dog won't drink. No I don't pay for this "FRESH WATER" individually but my annual slip fee provides me with this unlimited "FRESH WATER".
Tried blasting jellies out with high pressure hose nozzle to no avail. Decided to use undrinkable "FRESH WATER". We do use it for washing our vessels, however !
 
I wonder if the original poster is going to tell us what happened???
 
Sorry Bob. But it still seems like a waste. But considering the amount of water I use in my job, I'll just shut up now. :-)
 
Back
Top